strange intermittent power problem
Moderator: Harold_V
-
- Posts: 384
- Joined: Thu Jul 26, 2007 6:02 pm
- Location: michigan
Re: strange intermittent power problem
well it did indeed start to act up again. this time i skipped the spray-on contact cleaner and removed the wires from the switch and polished them and the lugs with an eraser. i needed to use an eraser just to reach them as the lugs are recessed inside a space maybe 1/2" diameter and about 1" deep. i did not have any anti oxident paste so they got snugged down good. one thing that i did notice was the identification for the closed circle crimped on conector had been stamped into the side that makes the connection. didn't seem like a good idea to me as it could leave an area not fully in contact with the surface. maybe causing arcing over time? time will tell whether it worked.
atlas 618,MM challenger wire welder, 4x6 cheapo bandsaw, assorted junk, spears for hunting mastadons.
-
- Posts: 112
- Joined: Sat Oct 15, 2011 6:45 pm
Re: strange intermittent power problem
This is all copper wire? No aluminum? I don't like aluminum because of it's constant unstable "cold flow" properties.
And it is #10 wire for 30 amps, correct?
Could a start capacitor be an issue somewhere in the circuit?
And it is #10 wire for 30 amps, correct?
Could a start capacitor be an issue somewhere in the circuit?
-
- Posts: 2938
- Joined: Sun Jun 27, 2010 10:43 pm
- Location: pendleton or
Re: strange intermittent power problem
i am left with the impression we are talking differient things
all wire connections must be tight but i suspect the switchs internal contacts not the lugs are the issue
to rule out the lugs turn off the power and measure resistance from the lug to the plug
all three should be the same 0.0 ohms
i also would take the cord end and recepticle and check all those connections if that applies
still no luck place 2 120 v light bulbe is series between phase to phase do this a phase to b and b to c with another set
shart moving checking running stuff if they blink or dim you will catch it and have a idea where to look
all wire connections must be tight but i suspect the switchs internal contacts not the lugs are the issue
to rule out the lugs turn off the power and measure resistance from the lug to the plug
all three should be the same 0.0 ohms
i also would take the cord end and recepticle and check all those connections if that applies
still no luck place 2 120 v light bulbe is series between phase to phase do this a phase to b and b to c with another set
shart moving checking running stuff if they blink or dim you will catch it and have a idea where to look
-
- Posts: 384
- Joined: Thu Jul 26, 2007 6:02 pm
- Location: michigan
Re: strange intermittent power problem
definitely bad contactor inside the switch/breaker. (infinite resistance on one when closed) this part is quite hard to find so far as it has a shunt trip attached to it. still polling our aftermarket suppliers for something on it. japanese printing press. searched e-bay and found one that had just ended and nothing else. not sure exactly what the shunt trip protects the unit from, but my guess is it cuts power in case of overload in the control circuits.
atlas 618,MM challenger wire welder, 4x6 cheapo bandsaw, assorted junk, spears for hunting mastadons.
-
- Posts: 2938
- Joined: Sun Jun 27, 2010 10:43 pm
- Location: pendleton or
Re: strange intermittent power problem
sound like the boss wants it running if a contactor wire a second contactor that is properly sized in parallel with the existing contactor that way the shut trip is still controlling and protecting the machine
it could also be set up to ensure that all power is removed when stop buttons are engaged
presses like to eat fingers
if this is a shunt trip breaker once you know the trip coils voltage(should be on the part) a different model can be subbed
all major breaker manf have these in their product line. they are used often tied to fire supression systems , gfi senser
modules as a couple examples
a third option would be a regular breaker with a contactor after the breaker
it could also be set up to ensure that all power is removed when stop buttons are engaged
presses like to eat fingers
if this is a shunt trip breaker once you know the trip coils voltage(should be on the part) a different model can be subbed
all major breaker manf have these in their product line. they are used often tied to fire supression systems , gfi senser
modules as a couple examples
a third option would be a regular breaker with a contactor after the breaker