Splicing Romex?

Topics include, Machine Tools & Tooling, Precision Measuring, Materials and their Properties, Electrical discussions related to machine tools, setups, fixtures and jigs and other general discussion related to amateur machining.

Moderators: GlennW, Harold_V

curtis cutter
Posts: 559
Joined: Fri May 18, 2012 11:46 pm
Location: Curtis, WA

Re: Splicing Romex?

Post by curtis cutter »

Remember there are a certain number of each gauge of wire each color of wire nut will hold. As previously mentioned, calculate your box fill. Romex must be fastened within 6" of the box unless clamped in the box. Leave 6" of wire ends in the box.
Gregg
Just let go of it, it will eventually unplug itself.
John Hasler
Posts: 1852
Joined: Tue Dec 06, 2016 4:05 pm
Location: Elmwood, Wisconsin

Re: Splicing Romex?

Post by John Hasler »

Also realize that the code just tells you how many wires you are allowed to *try* to get into a given size box. Make things easy on yourself and use oversize boxes. The job will go faster and you will have room for expansion.
User avatar
SteveHGraham
Posts: 7788
Joined: Sat Jan 17, 2009 7:55 pm
Location: Florida

Re: Splicing Romex?

Post by SteveHGraham »

The existing wiring is on top of the walls and trusses, and the builders dropped it down into the cinderblocks. This allowed them to have flush-mount boxes for the owner to plug into.
Every hard-fried egg began life sunny-side up.
curtis cutter
Posts: 559
Joined: Fri May 18, 2012 11:46 pm
Location: Curtis, WA

Re: Splicing Romex?

Post by curtis cutter »

SteveHGraham wrote: Fri Sep 06, 2019 10:00 am The existing wiring is on top of the walls and trusses, and the builders dropped it down into the cinderblocks. This allowed them to have flush-mount boxes for the owner to plug into.
So the cinder blocks contain no rebar or concrete or is it in conduit encased in concrete?
Gregg
Just let go of it, it will eventually unplug itself.
User avatar
SteveHGraham
Posts: 7788
Joined: Sat Jan 17, 2009 7:55 pm
Location: Florida

Re: Splicing Romex?

Post by SteveHGraham »

There is no conduit. It's just cinderblocks and wire in the cavities.
Every hard-fried egg began life sunny-side up.
spro
Posts: 8016
Joined: Mon Feb 20, 2006 11:04 pm
Location: mid atlantic

Re: Splicing Romex?

Post by spro »

If the outlet box is steel, there are other boxes which "piggy back" on to their face. These boxes are open at the back, allowing wiring and wire nuts. They can also be larger than the standard one, allowing a switch or duplex. Since they are larger, there holes to mount them ( via simple anchors) to the wall securely.
John Hasler
Posts: 1852
Joined: Tue Dec 06, 2016 4:05 pm
Location: Elmwood, Wisconsin

Re: Splicing Romex?

Post by John Hasler »

So they cut the boxes into the block?
spro
Posts: 8016
Joined: Mon Feb 20, 2006 11:04 pm
Location: mid atlantic

Re: Splicing Romex?

Post by spro »

Good point John. So they did what? I'm just trying, same as you. He said they are flat to the wall.
SLK001
Posts: 8
Joined: Tue Jan 29, 2019 8:53 pm
Location: Coral Springs, FL

Re: Splicing Romex?

Post by SLK001 »

The better way is to connect the existing wire to the new wire and pigtail to the current outlet (three wires in a wire nut). Do this for the hot, the neutral AND the ground. And all this has to be in a box.

As for what you are calling Romex, it's armored cable, right? Does it have a separate ground wire? Armored cable would be to code, but regular house wire would not, if exposed.

Conduit would really be the way to go.
spro
Posts: 8016
Joined: Mon Feb 20, 2006 11:04 pm
Location: mid atlantic

Re: Splicing Romex?

Post by spro »

BX is armored cable type but thanks for input to the discussion. There are reasons for the many types but heck, what about roof leak, where the top junction fills with water.
Patio
Posts: 1369
Joined: Wed Oct 06, 2010 3:14 pm
Location: Centralia Wa

Re: Splicing Romex?

Post by Patio »

A simple rule of thumb. If you can put a fork in your hand and stab a wire, it is done wrong!
If you go by NEC code, all wiring must be protected up to 8" from the floor, by a wall covering or conduit. The romex that is fished over the rafters and down into the cinder block, to the box that is flush mounted with the surface of the wall, is fine.
If it were mine, I would install one of these on the exiting box,
https://www.homedepot.com/p/Steel-City- ... /206465546
Then run conduit down the wall, PVC or EMT to the next box, one like the one above, but without the hole in the back.
Or you can cut the wire in the rafters to create a splice, by installing a nail-on type box, and putting the splice inside the box. Run wire from that box to the new out let and to another nail-on box, also in the rafters, closer to the original, allowing slack for a second splice to pick up the wire for the original outlet.
I am a electrical contractor by trade, if you want to talk, send me a PM.
Live for the moment!
Prepare for tomorrow!
Forgive the past!
TomB
Posts: 495
Joined: Mon Jan 14, 2008 7:49 pm
Location: Southern VT

Re: Splicing Romex?

Post by TomB »

It frequently is easier to add a sub panel on the wall near the new outlets. Then you only need to run a single wire from the original panel to the new panel. In my case I brought a 220v line from the old to the new then split it to some 120v and a couple of 220v outlets.